Are we allowed to use 5 amp fuses in 13 amp plugs? | on Free Electrical Advice - Electricians Forums (2024)

Discuss Are we allowed to use 5 amp fuses in 13 amp plugs? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

M

mark641

-
Reaction score
11
  • Sep 12, 2020
  • #1

I work for a charity (Besom) that gets equipment that needs to be PATted. A lot of these come with 5 amp fuses. Please do the regulations
allow you to use 5 amp fuses, or are you supposed to change them to 3 amp? Most of these devices are low power & they will run perfectly
well on a 3 amp fuse.

But the latest device is different. It is a Morphy-Richards iron model 42680. This has a 5amp fuse & is rated 6amp. I would like to change this to a 13amp fuse, but how do I tell if the cable will carry this?

Thank you, Mark

Dartlec

Esteemed

Arms

Reaction score
2,439
  • Sep 12, 2020
  • #2

mark641 said:

I work for a charity (Besom) that gets equipment that needs to be PATted. A lot of these come with 5 amp fuses. Please do the regulations
allow you to use 5 amp fuses, or are you supposed to change them to 3 amp? Most of these devices are low power & they will run perfectly
well on a 3 amp fuse.

But the latest device is different. It is a Morphy-Richards iron model 42680. This has a 5amp fuse & is rated 6amp. I would like to change this to a 13amp fuse, but how do I tell if the cable will carry this?

Thank you, Mark

This page may be helpful: - Manufacturers have now standardised ratings to either 3A or 13A - I believe these have always been the only ones that were 'officially' in the standard, though other ratings were quite widely used, including the 5A.

From that site:

Manufacturers have now standardised plug fuse ratings to be either 3A or 13A. However, 5 Amp fuses are still used in some older equipment and are available to buy.

Which isn't terribly helpful in your case.

Where does it state 6A as the iron rating? If it comes with the manual then the manufacturers instructions should be followed as they designed it. It is also sometimes moulded into the plug. Having said that, there is no 6A fuse, and 10A fuses are available but used rarely in my experience.

It may be difficult to determine the cable size if it is a moulded plug, though some flexes do say the conductor size on them (2 x 0.75, 3 x 1.5) etc. It would probably need to be 1.25mm2 in size or larger to safely be protected by a 13A fuse.

Having said that, a "6A" (In reality it will be rated in Watts) iron is unlikely to blow a 5A fuse in reality. The factor is about 1.6, so a 5A fuse would likely blow at 8A or so.

James

-

Staff member

Mentor

Esteemed

Arms

Supporter

Patron

Reaction score
9,364
  • Sep 13, 2020
  • #3

Remember, the fuse is there to protect the cable to the appliance.
If there are sensitive parts inside the appliance that can’t survive an over current protected by the plug, they should be protected by a fuse or similar within the appliance.

BS 1362 allows for any rating of fuse up to 13A
However, normally the ones available are
1,2,3,5,7,10 and 13A

So in the absence of manufacturers data, any fuse that is marked as compliant with BS 1362 AND
a low enough rating to protect the cable in event of a fault
A high enough rating to power the full load of the appliance continually
Take into account short duration surges and where possible not blow on something like a filament rupture of a lamp.

Would be acceptable in my opinion.

You say, lots of equipment comes to you with 5A fuses and you change them for 3A fuses.
I don’t see the reasoning behind this unless the cable is under 0.75mm sq.

Vortigern

Esteemed

Arms

Reaction score
2,391
  • Sep 13, 2020
  • #4

Hi @mark641, may I ask, do you have C&G 2377? I ask because if you do not it is debatable as to whether you should be PAT testing. I am a little worried that you want to modify equipment when you are not sure about what you are doing? What rating is the iron? Let us imagine it is 2800 watts, So 12.2 A. It is likely a 5A fuse for that rating will blow, but it seems it came with the fuse so assuming it was in use there is a bit of a puzzle as to why that rating was in the plug. Maybe it is not 2800 watts so there is not a mystery. But in any event if the appliance is rated as 6A then I would be very careful about changing the characteristics without having an understanding gained from training.
Please do not take this as a criticism I absolutely support charity workers and think you do a wonderful job. It is just that I have seen in charity shops, people using a PAT machine and pressing the button and putting a label on and putting it up for sale when there are say frayed cords or other damage not seen by the person in question.

Julie.

Esteemed

Arms

Reaction score
4,815
  • Sep 13, 2020
  • #5

If you are portable appliance testing, you at the very least need to understand the processes & criteria for acceptance and have to hand the code of practice which documents these.

Table 10.6 in the cop shows which fuses are generally used (including 5A) and where they are used.

Primarily if the appliance/manufacturer states 5A, or 3A and so on, that's what should be fitted.

However if the cable size is smaller than in table 10.6 for the fuse size then the cable needs replacing as the fuse is unsuitable for the cable.

So, an appliance states 13A fuse, but the cable is 0.5mm^2 then although a 13A fuse fitted would be appropriate for the appliance, it is too big to protect the cable (table 10.6).

Therefore it cannot pass pat unless it is repaired with the correct cable.

In your case, therefore it depends what size fuse is stated by m.r. for this iron charger and the cable size (although if the cable is original it's likely to be suitable)

Last edited:

pirate

-

Esteemed

Arms

Supporter

Reaction score
5,592
  • Sep 13, 2020
  • #6

Of course you are "allowed", but you need to be sure that the fuse you select is appropriate. I also do testing for a charity and we have lots of power tools donated. The usual rule applies...if it came with a 3A fitted and it works, leave it alone. However, it goes a lot further than that...
A very common tool we receive is an older style hammer drill, often about 750W, and almost always they have a 5A fuse fitted. They are fine, takes a bit of overload, fitted by the manufacturers, leave it alone too, imho.

P

pc1966

Esteemed

Arms

Reaction score
12,161
  • Sep 13, 2020
  • #7

I guess it might have changed, but it used to be common to have 5A on lower power electronics like PC, etc, to allow for the switch-on surge not blowing the fuse.

telectrix

-

Mentor

Esteemed

Arms

Reaction score
67,048
  • Sep 13, 2020
  • #8

what's wrong with cutting the head off of a 1" roofing bolt. fits perrf*ck.

J

Julie.

Esteemed

Arms

Reaction score
4,815
  • Sep 13, 2020
  • #9

telectrix said:

what's wrong with cutting the head off of a 1" roofing bolt. fits perrf*ck.

The cut end would go rusty!

telectrix

-

Mentor

Esteemed

Arms

Reaction score
67,048
  • Sep 13, 2020
  • #10

Julie. said:

The cut end would go rusty!

dang gosh darnit. forgit to mention the IP 67 plug (top).

Z

Ziggie

Reaction score
55
  • Dec 11, 2020
  • #11

telectrix said:

what's wrong with cutting the head off of a 1" roofing bolt. fits perrf*ck.

You could do that and then make a bolt for the door

Pete999

-

Esteemed

Arms

Reaction score
17,071
  • Dec 11, 2020
  • #12

Ziggie said:

You could do that and then make a bolt for the door

Seen a live 0.22 cartridge as a link once at a RAF MQ

Pete999

-

Esteemed

Arms

Reaction score
17,071
  • Dec 12, 2020
  • #13

Pete999 said:

Seen a live 0.22 cartridge as a link once at a RAF MQ

True though

Z

Ziggie

Reaction score
55
  • Jan 21, 2022
  • #14

Pete999 said:

Seen a live 0.22 cartridge as a link once at a RAF MQ

And an even better instant.
An I.T. company selling recovery solutions sent a dummy bullet to potential customers stating " if you dont have proper recovery procedures in place , you might as well use the enclosed. They sent it to customers in Northern Ireland during the troubles.
This was not well received.

Reply to Are we allowed to use 5 amp fuses in 13 amp plugs? in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

B

Plugs and Fuses - Help understanding symbols (PC/Monitor)

The same socket can be used for different appliances, such as kettles... which will draw more than 5AThe size of the cable determines how much...

  • Barney1234
  • DIY Electrical Advice
  • 4
  • 702
  • fuseshelpplugsunderstanding
Replies
4
Views
702

Mar 5, 2024

littlespark

B

PAT Testing 3 phase to 13amp adapter leads

Ok perfect much appreciated for the response will go with that connection 👍

  • Buzz1980
  • 17
  • 3K

2

  • 3 phaseadapteradaptorsleadspatpat testingphasetesting
Replies
17
Views
3K

Sep 26, 2022

Buzz1980

B

S

  • Locked
  • Solved

Thx to the forum over the years

Therein lies the problem.I see no merit in further circular debate, so will bow out of this discussion.

    • Are we allowed to use 5 amp fuses in 13 amp plugs? | on Free Electrical Advice - Electricians Forums (10)
  • Steve-S
  • UK Electrical Forum
  • 55
  • 6K

234

  • the forumyears
Replies
55
Views
6K

Aug 15, 2023

nicebutdim

  • Question

A Thread About Boring Old Plugs And Fuses

Those 9mm MCBs are rather small, as are the little push button panel mount thermal circuit breakers.

  • OnlQQker
  • UK Electrical Forum
  • 5
  • 2K
  • 13 amp5 ampfusesoldplugsthread
Replies
5
Views
2K

Mar 7, 2020

freddo

Pat testing plug fuses

cheers i have just ordered one ..handy visual effect to show anyone that the plug is fake

  • sham
  • 29
  • 8K

2

  • fusespatpat testingplugtesting
Replies
29
Views
8K

Feb 26, 2018

DC-backfrom the past

Are we allowed to use 5 amp fuses in 13 amp plugs? |  on Free Electrical Advice - Electricians Forums (2024)

FAQs

Can I use a 5amp fuse in a 13 amp plug? ›

Yes, the plug is rated for up to 13A but can be less to suit your needs. If it was the other way around, putting a 13A fuse in a 5A plug, then you'd be in trouble. That is generally not a good idea. The fuse is there for protection in the event something goes wrong.

Are 5 amp fuses still used? ›

5-amp fuses are still found in some older equipment, but this is no longer a standard size.

What is the difference between a 13A and a 5A fuse? ›

5A fuses are suitable for electrical devices with a maximum 1250w wattage such as televisions, hairdryers, vacuum cleaners etc. 13A fuses are suitable for electrical devices with a maximum 3250w wattage such as fridges, freezers, washing machines, irons, toasters, kettles etc.

Can you put a 3 amp fuse in a 13amp plug? ›

The British Standard for plugs, BS1363, has standardised on just two preferred fuse ratings, 3A and 13A, however, any fuse rating up to 13A can still be used. 3A fuses are marked in red and 13A fuses are brown. Fuses are also available in 1A, 2A, 5A, 7A & 10A sizes and are marked in black.

Can I put a 5A fuse in a 10A plug? ›

Can I put a 5A fuse in a 10A plug? - Quora. Yes. If the nominal current draw is lower than the fuse ratting. UK 13 amp plugs can be fitted with a wide range of fuses to better match the load of the thing they are fitted to.

Can a 5amp fuse instead of 3A? ›

If you replace it with a 5A fuse you will lose part of the protection the 3A fuse was intended to provide. In case of a failure of the device the fuse is suppose to protect, the result of using a larger fuse could be to damage the device to the extent that it could not be repaired. It could also start a fire.

When to use a 5amp fuse? ›

5 amp sockets are used on the lighting circuit, meaning they are switched on and off with the light switches in the room, rather than being used like regular plug sockets. They are designed for appliances that take less than a 5 amp current, for example floor lamps, table lamps and fans.

What plugs have 5A fuses? ›

5 amp 240 volt plug top fuse. The BS1362 plug top cartridge fuse is the most common type of fuse, as it is mainlyused in a variety of household electrical appliances from toasters to kettles, to laptop chargers and televisions.

When did electricians stop using fuses? ›

A: Fuse panels stopped being used within homes in the 1960's. This means the rest of your electrical service (meter socket, outside overhead riser) is likely equally old.

Why can't A 5A fuse be used in wire carrying 15a current? ›

It happens so because as soon as the current in the circuit crosses 5A, the fuse will melt thus discoonecting the whole circuit.

Can I replace A 5A fuse with A 6a? ›

If you replace a fuse with a higher amp, the new fuse will not interrupt the current in time, when it becomes too high, resulting in overheating, damaging insulation (= danger of electrocution), or even a fire.

Can I use A 10amp fuse in A 13 amp plug? ›

Can you replace a 13 amp with a 10 amp? Certainly you can. The problem is that if what ever is hooked up to that circuit draws more than 10 amps, you will blow that 10 amp fuse. If this circuit uses less than 10 amps, you will be OK.

What happens if you use a 13 amp fuse instead of a 5? ›

The 5A fuse protects the cable and/or the device which is connected via the plug to the mains. If you replace it with a 13A fuse, it may work if cable and device are in OK condition. But the protection effect is gone. If the device or the cable are defect or short circuited or similar, there may be a fire hazard.

What size fuse for a 13 amp plug? ›

13 Amp / 13A plug top fuse (the highest rating fuse that can be fitted to a UK plug top), made to the British Standard BS1362. Dimensions : length 25.4mm (1 inch), diameter 6.3mm (1/4 inch).

What will happen if I use a 5 amp socket for a 2000 W equipment? ›

Assuming you are on a 220V-240V household system, your 5 amp circuit will support 1100–1200W of power, so as soon as your equipment draws more than than 5A the breaker or fuse will trip and you will be in the dark.

Can you put a 10amp fuse in a 13 amp plug? ›

Can you replace a 13 amp with a 10 amp? Certainly you can. The problem is that if what ever is hooked up to that circuit draws more than 10 amps, you will blow that 10 amp fuse. If this circuit uses less than 10 amps, you will be OK.

Can you put any amp fuse in a plug? ›

Some appliances (such as your TV) may need a 5 amp fuse, but always check the appliance manufacturer's instructions first. Make sure the fuse you use has the right rating. For the convenience of users, appliance manufacturers have standardised to two plug fuse ratings- 3A & 13A and adopted appropriate flex sizes.

References

Top Articles
Latest Posts
Article information

Author: Mr. See Jast

Last Updated:

Views: 6452

Rating: 4.4 / 5 (75 voted)

Reviews: 90% of readers found this page helpful

Author information

Name: Mr. See Jast

Birthday: 1999-07-30

Address: 8409 Megan Mountain, New Mathew, MT 44997-8193

Phone: +5023589614038

Job: Chief Executive

Hobby: Leather crafting, Flag Football, Candle making, Flying, Poi, Gunsmithing, Swimming

Introduction: My name is Mr. See Jast, I am a open, jolly, gorgeous, courageous, inexpensive, friendly, homely person who loves writing and wants to share my knowledge and understanding with you.